About 50 results
Open links in new tab
  1. Acceptable stati pressure for return and supply - HVAC-Talk

    Nov 21, 2018 · A lower static pressure will mean improved performance for your equipment. High efficiency equipment alone does not provide home comfort and efficiency. Home Performance takes …

  2. Building Static pressure - HVAC-Talk

    May 14, 2011 · I need to install a differential static pressure senser to control building static 1st part of my question, does the high pressure pitot tube go to the outside and low pressure pitot goes on the …

  3. Static Pressure Reset ? | HVAC-Talk: Heating, Air & Refrigeration ...

    Oct 21, 2022 · what is the purpose of resetting static pressure setpoint? don't he VFD's back down anyways once the dampers start closing after reaching room setpoint with a set static pressure …

  4. static pressure design goal - HVAC-Talk

    Aug 2, 2006 · For a new system - 5 ton heat pump, what should be the design goal for the total static pressure? (filters, coil, ductwork, and vents) I'm guessing that it should be somewhere around .4 to …

  5. Maximum static pressure - HVAC-Talk

    Sep 3, 2005 · The maximum external static pressure is usually around .5" W.C. but varies between manufacturers. Since you are looking into furnaces that have V.S fans in them it will give you more …

  6. Questions about Mobile Home Duct Static Pressure - HVAC-Talk

    Nov 12, 2008 · Im an HVAC Tech. Havent worked on Mobile Homes but want to start. I understand that these duct systems are higher in static pressure due to thier smaller size (typically 14x4" trunk …

  7. Stumped on calculating supply static pressure with... - HVAC-Talk

    Jan 22, 2026 · Sum (add together) the static pressure of each duct off the plenum (let's call this "Sum Supply scenario) Use the duct with the highest static pressure as your supply static pressure (let's …

  8. Static Pressure...... | HVAC-Talk: Heating, Air & Refrigeration Discussion

    Oct 2, 2004 · Ductwork configuration selection based on cfm required and static pressure used up for each area of ductwork and the total static of all of those, not to exceed the manufacturers maximum …

  9. Static Pressure. | HVAC-Talk: Heating, Air & Refrigeration Discussion

    Oct 3, 2011 · One of the measurements I make during Heat inspections is that of static pressure. The ideal static measure is: l 0.5l inches of water. So in a balanced return vs. supply it should be: l-0.25l + …

  10. Static pressure across the evaporator coil? - HVAC-Talk

    May 27, 2013 · Static at various cfm's and I think it's dry coil. "Pressure drop across the dry evaporator coil: An easy way to quickly verify airflow is to measure the static pressure drop across the …